Hello to all.
I was reading over current unbalance for three phase induction motors, but I don´t found which is the % acceptance of unbalance.
Someone can help me please, I must to define this % for a motor of compressor:

Data motor is:
400 V Delta
160 A
90 KW
1480 RPM

Is there some criteria or regulation defined for this?

thanks a lot
 
Posts: 29 | Location: Concepción, Chile | Registered: 15 June 2006Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Other than the specific criteria of no more than 7% current unbalance by the NEMA MG-1 in a controlled testing environment, there are no specific standards that cover current unbalance that I am aware of. The primary issue that has been covered in most standards is voltage unbalance, in which the maximum unbalance is 5%, with the motor de-rated, and under 2% without de-rating the motor.

Sincerely,
Howard


Howard W Penrose, Ph.D., CMRP
President, SUCCESS by DESIGN Reliability Services
Author: "Physical Asset Management for the Executive (Caution: Don't Read this on an Airplane)" and;
"Electrical Motor Diagnostics: 2nd Edition"
 
Posts: 803 | Location: Connecticut | Registered: 12 April 2005Reply With QuoteEdit or Delete MessageReport This Post