This is a 150hp screw compressor motor that was running fine. We were checking the power quality when the amp load went to a locked rotor level and the fuses blew. Any ideas why? After checking everything and replacing the fuses, the unit started and ran without issue. This is a wye start-delta run. Any ideas why the amps went so high? I hope the attachments went well.
![]() |
|||
|
That's a weird one all right.
If current goes to locked rotor amps but there's no machine damage, I would guess the load torque had exceed motor breakdown torque:
Those might be longshots, but it's all I can think of. |
||||
|
Lake Man
Check the timer in your starting circuit. If you remained in wye, then the motor was operating undervoltage. Another possibility is that the starter dropped back into wye for some reason. Howard Howard W Penrose, Ph.D., CMRP President, SUCCESS by DESIGN Reliability Services Author: "Physical Asset Management for the Executive (Caution: Don't Read this on an Airplane)" and; "Electrical Motor Diagnostics: 2nd Edition" |
||||
|
MotorDoc- The compressor had been running for a couple of days at the time it happened. The compressor next to it fried the drive that it runs on and we were checking the power quality to look for problems. This compressor does not use a drive just cross the line. We thought about it going back into wye, but it has a mech. interlock.????
|
||||
|