Go
New
Find
Notify
Tools
Reply
  
-star Rating Rate It!  Login/Join 
Posted
Industry standard documents specify a minimum bearing insulation resistance of 10 megaohms (EASA AR100) or 1 megaohms (EPRI 1000897) when tested at 500vdc. These limits apply for motor refurbishment. What limit would you consider appropriate for motors tested while installed (not recently refurbished).

This specific motors in question is aa group of large vertical motors (non-vfd) that drive a vertical pump through a rigid coupling. Both top/bottom bearings of the motor are insulated.

We routinely remove these motors to get access for pump work (the pump bearings have had a lot of problems, although none has been specifically attributed to shaft current).

When the motor is removed, we do an insulation resistance test. Typically the insulation is < 1 megaohms. Sometimes we can improve it by cleaning / inspecting easily accessible areas. Sometimes we can't get it above 30 k-ohms without disassembling the motor.

Are there any standards that address this situation?

Does anyone know typical ranges of shaft voltages and how much current is required to cause damage? (might use this to guesstimate min acceptable resistance)
 
Posts: 3063 | Location: Texas Gulf Coast | Registered: 20 February 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
quote:

Does anyone know typical ranges of shaft voltages and how much current is required to cause damage? (might use this to guesstimate min acceptable resistance)


Talking about the non-vfd motor, the induced voltage must be caused by asymmetry of the flux. In case of the 2-pole motor (which is the easiest to imagine) it would be the difference between the flux going on one side of the shaft compared to the other side (of the shaft). Hence the voltage must be substantially lower than the turn-to-turn voltage (shaft, bearings, endbels and frame of the motor constitute a one turn). One can imagine a 1000 hp motor with turn-to-turn about 25 Volts. From that I arrive at voltages very likely below 1 Volt. I have never measured it, but the resistance of 30 kOhms seems to be plenty good to me.
jank
 
Posts: 164 | Location: alberta, canada | Registered: 04 September 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Pete,
What I have come across: typical ranges of shaft voltages are: 100 mVac .. 1.0 Vac, frequency 1* .. 6* Fline and/or 1*RBPF depending on elec/mech/magnetic asymmetry in design of asynchronous, synchronous or dc machine, kW .. MW range.
Shaft short-circuit current may range from 10 mA to 10 A, same frequency, also depending on design.
Since frequency range is pretty low, say 50 hz .. 60 hz up to 1 khz .. 2 khz an actual (Al2O3 ceramics) insulation resistance of 30 kohm is enough to reduce shaft circulating current to much less than 1 mA and this is I conguesstimatesider as safe.

As far as I know there are no standards for installed machines.

But be carefull when modern vfd is involved. For very high spikes from the rapid dU/dt switching the insulator may behave as a capacitor and will conduct current. This type of shaft current ranging from 100 khz into Mhz is, I am almost certain, not yet covered by standards. I have already seen several insulated bearings that are not insulating (vfd applications only) resulting in damaged bearings because of electrical current.

Q: can you tell us how you measure that insulation resistance? With machine running, uncoupled, no-load, using shaft riders, what voltage you apply?

Regards,
Arie Mol, NL
Rotating Equipment Consultant
 
Posts: 133 | Location: Wierden, Netherlands | Registered: 06 March 2006Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Thanks Jan and Arie for your responses.

I will mention there is another thread I started on another forum addressing the same question.

http://www.eng-tips.com/viewthread.cfm?qid=208967&page=1

In there you'll see among other things a link to an article on ths subject
http://www.netaworld.org/files/ItemFileA340.pdf
Still doesn't shed a tremendous amount of light.

The motors I am interested in are not vfd driven.

We test bearing insulation resistance with the machine secured and motor uncoupled using a 500vdc megger. (You'll note this matches the standards cited in my original post). We check from shaft to frame (the uninsulated portion of the frame which excludes lower bearings housing... in this case lower bearing housing is in contact with lower beianrg but inulated from lower bearing bracket and the rest of the frame). It works for this particular motor because both upper and lower bearings are insulated.

I do notice that several large reputable OEM's has given very low limits for machines with sliding bearings. For example Westinghouse identifies 3 kohms minimum for a group of our critical sliding bearing motors. I am not sure I can extend these values to rolling bearing motors. It seems to me that sliding bearing motors have a built in insulator at the bearings in the form of an oil wedge while running... not the case for rolling bearings.
 
Posts: 3063 | Location: Texas Gulf Coast | Registered: 20 February 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Pete,
Two comments:
1)
<qoute>It works for this particular motor because both upper and lower bearings are insulated.<unquote>.
Yes, but what to do when only one bearing is insulated, then it does not work right? Not many motors have both bearing insulated!
My trick: Under normal (any) running conditions, short-circuit the nde shaft to ground with a shaft rider and a 2.5 mm2 cable. Than measure the current with a clip-on ammeter. Also measure the shaft voltage over both shaft ends. Good old Ohm's law tells you the impedance of the bearing insulation (= ceramic bearing insulation + oil film insulation) of de end bearing arrangement. If current is zero then bearing isolates perfectly.
Analogous for short-circuiting the de shaft.
2)
<quote>It seems to me that sliding bearing motors have a built in insulator at the bearings in the form of an oil wedge while running... not the case for rolling bearings.<unquote>.
Yes, but rolling element bearings have an oil film too!! What else would be the lubrication mechanism?
Above mentioned test methode will reveal that clean oil in rolling element bearing provides an insulator. Contaminated oil (carbon, steel wear particles) will show up impedances in MOhm .. kOhm range or even lower.

Regards,
Arie Mol
 
Posts: 133 | Location: Wierden, Netherlands | Registered: 06 March 2006Reply With QuoteEdit or Delete MessageReport This Post
 Previous Topic | Next Topic powered by eve community  
 