Posted
Our 55 MW Steam turbine is witnessing high -ve axial shift (-0.55) mm & high -ve differential exp.(-2.50) mm at full load. Set value of axial shift is 0.55 mm with design tolerance (-1.7 mm towards front of turbine & +1.2 mm towards generator) & differential expansion design limit is +3.0 to -2.5mm.
Turbine pads (thrust & surge) temperature is normal with drain oil temperature within limit. What could be cause behind such a high -ve values of axial shift & differential expansion ?? Does generator magnetic off-set play any role behind this problem, if we set this value beyond lower or upper design limit of magnetic offset ???
regards
kamnesh
 
Posts: 7 | Location: india | Registered: 31 March 2009Reply With QuoteReport This Post
Posted Hide Post
Pl. check if your zero point for the proximity probe is correct.
Regards
Irshad
 
Posts: 556 | Location: INDIA | Registered: 14 March 2007Reply With QuoteReport This Post