I have problem, induction motor last measured 28 dB down, when i am checked now db increase above 41 dB ( measure with CSI 2120 by clamp current)
Motor data : 3,3KV, 500KW, 1485, 90Amp rpm motor run parellel with some motor (any 2 motor run for drum barker) but current not same & diffrent above 15 amp


MCSA......is new revolution on electrical
 
Posts: 3 | Location: Jambi Indonesia | Registered: 30 December 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
28db down pole pass sidebands are a bad symtpom.

If the loading were less in the second test, that could explain why the sideband magnitude went down (db difference went up).

You should have load data available. If nothing else you can extract it from the magnitude of the line frequency peak in your sepctrum.
 