This happen at 700MW generator and exciter only, the 1X fluctuating every 50 minute, Any idea? what is the root cause
Trend.pdf (291 Kb, 31 downloads) |
|||
|
I would start with considering a seal rub.
Michael Titone |
||||
|
Ahmad,
The measurement point says "EXC", so I assume the measurements are on the exciter. If that is the case, then I would consider a exciter brush rub. I worked on a 450-MW Alstom T-G with this problem. Walt |
||||
|