This happen at 700MW generator and exciter only, the 1X fluctuating every 50 minute, Any idea? what is the root cause

PDF DocTrend.pdf (291 Kb, 31 downloads)
 
Posts: 29 | Location: Kuala Lumpur | Registered: 02 July 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
I would start with considering a seal rub.

Michael Titone
 
Posts: 59 | Location: Southeast USA | Registered: 20 February 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Ahmad,

The measurement point says "EXC", so I assume the measurements are on the exciter. If that is the case, then I would consider a exciter brush rub. I worked on a 450-MW Alstom T-G with this problem.

Walt
 
Posts: 1084 | Location: Massachusetts | Registered: 27 April 2005Reply With QuoteEdit or Delete MessageReport This Post