Yesterday I tested a McQuay roof top air handler. The vibration at the outboard fan bearing was 3.4"/sec, at fan speed. I inspected the fan and structure for something broken and found nothing. In the process of turning the fan, I thought I heard water sloshing. I turned it a few more times and determined that a blade seemed to contain water. We drilled some small holes in the blade and the water came running out. Now the fan speed vibration is .27"/sec. Not a clue how the water entered this particular blade. The blade is a stainless steel air foil.
Posts: 163 | Location: US | Registered: 26 May 2005
Yea, I had this issue on a 1500 hp induced draft fan. Balance weight calculation indicated over 10-lbs. I saw water weeping over the backing plate and had holes drilled into every (12) blade to be sure. It was easier to balance afterwards!
Walt
Posts: 1563 | Location: Massachusetts | Registered: 27 April 2005
Perhaps at some point the fan was 'off' and maybe rainwater entered from the top and ran down onto (and into) the bottom blade? Anytime I have high imbalance on a fan I like to do a "rock down" test if possible to determine if there is an obvious heavy spot, and if so, I try and see why it might be heavy. On belt-driven fans, I drop the belts off if possible before doing this.
Regards,
Rusty
"The trend is your friend."
Posts: 1734 | Location: Arkansas | Registered: 20 February 2005
I have not seen water, but I have seen fly ash and coal dust inside foil type blades on ID/FD/PA fans on boilers. A bump test helped us to identify which blades were affected.
Bill Kilbey google voice # (865) 686-6050 bkilbey@gmail.com
Posts: 353 | Location: Knoxville, TN USA - The center of the reliability universe! | Registered: 06 May 2007