Does any one know of any articles on the proceedure for taking Transformer oil samples and maybe a list of do and do nots?
Also does anyone know the best way to get rid of old transformer oil? |
|||
|
Maybe DOE or Noria websites contain this informstion.
|
||||
|
A few links:
http://www.netaworld.org/files/ItemFileA434.pdf http://www.nttworldwide.com/docs/sampling.pdf Also you might ask for instructions from your lab especially if they provide you with syringes. That would also include handling of the sample syringes after they're drawn. A few thoughts: Never try to sample an energized instrument transformer. (CT or PT). It may cause a violent explosion. Stay away from sampling deenergized bushings unless you really know what you're doing with respect to cleanliness. Check for indication of positive pressure before you open a sample valve. There's no substitute for training. |
||||
|
Mike,
I tried to call you several times today to discuss the Transformer Oil testing. Please email me when it may be a good time to call you. smithj@ivc-pdm.com Jim Smith IVC |
||||
|
PredictUSA may also be a source. Check 'em out and ask for Doug Holmes.
Cordially, Sam |
||||
|
1)Read ASTM D3613-98 and ASTM D 923-97
2)Neta has two or three interesting articles on this matter. See electricpete's post above. Regards Claudio |
||||
|