Hi every body.....
Small diesel engine genrators (8 MW each) are connected directly to 13.8KV busbar and a tie breaker (NO) is located between them.
Both generators are working properly when the tie breaker is open. But when the tie breaker colsed , Both generators tripped by circulating currents.
Please share your opinions
Your recommendations are highly appreciated.
Best regards Eeker
 
Posts: 3 | Location: JEDDAH | Registered: 20 March 2006Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Is this a new installation or a new phenomenon with an old installation that had previously synched properly?

John
 
Posts: 340 | Location: Exton PA | Registered: 22 February 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Try checking for any difference in the generator terminal voltages, frequencies or phase angles. Normally, this is taken care of by the synchronizing relay. So better test the relay for its proper functionality.

Does the problem occur when a particular genertor is being brought online? If so, the excitation response droop of that generator needs adjustment.
 
Posts: 5 | Location: Pakistan | Registered: 20 April 2004Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
quote:
Originally posted by engmousa:
Hi every body.....
Small diesel engine genrators (8 MW each) are connected directly to 13.8KV busbar and a tie breaker (NO) is located between them.
Both generators are working properly when the tie breaker is open. But when the tie breaker colsed , Both generators tripped by circulating currents.
Please share your opinions
Your recommendations are highly appreciated.
Best regards Eeker

iS IT SOMETHING TO DO WITH DROOP MODE OR ISOCHRONOUS MODE RUNNING OF THE GENERATORS?
 
Posts: 210 | Location: INDIA | Registered: 14 March 2007Reply With QuoteEdit or Delete MessageReport This Post