Posted
Hi
I would like to know what tests should be performed in a repaired motor to assure the repair was done correctly and motor is running properly. Could you please list a set of tests to be performed/standards of reference. Thanks
Motor is:
2250 HP
50 Hz
3 phase
6 kV
330 RPM
 
Posts: 10 | Location: Argentina | Registered: 02 May 2006Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Test to be run depends on what was repaired?


Darth Eugene Vader
 
Posts: 1041 | Location: Puerto Rico, USA | Registered: 28 October 2005Reply With QuoteEdit or Delete MessageReport This Post
VJG
Posted Hide Post
If the repair involved anything that could possibly damage the stator core (e.g. remove rotor, rewedge, rewind), it should be tested for shorted laminations to avoid overheating when put back in service. A loop test at full rated flux or low flux Motor Core Tester from us (ADWEL) could be used.
 
Posts: 3 | Location: Toronto, Canada | Registered: 30 August 2006Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Hi Claudio. As has been stated, it depends on what has been "repaired".
Has it been rewound? Has it been stripped, cleaned, etc.? So many possibilities.
Whilst you have the oportunity on a large motor like this, you should check everything that cannot be checked during service such as insulation - phase to phase and to earth. If the rotor is out, check the wedging on the stator. Check the rotor-bars for cracking at the end-ring joints. Check the bearings. Check everything! You may not get another opportunity for years!
 
Posts: 152 | Location: Somerset. England | Registered: 22 August 2006Reply With QuoteEdit or Delete MessageReport This Post